    Hi all,
    Recently had our pool finished and the pool guy told me to get an electrican to hook the lights up. He made a point that he must make sure that the earth wire is also connected. There is an earth wire at the end of the pool just sticking out of the ground but Im just curious as to what this is required for being it is basically earthed already? What is this wire connected to any way?

  2. #2
    rrich Guest

    Default

    The earth wire should be connected to three things.
    A ground rod a couple of meters into the earth,
    The cold water plumbing system, and
    The ground bar inside the service panel. (Circuit breaker box)

    If the earth wire is connected to the earth or grounding system of the house, that should be sufficient. (The house earth system should already be connected safely.) I would not run two separate earth systems, one for pool and one for the house. There is the possibility of different earth potential and with a wet environment it may be hazardous.

  3. #3
    Join Date
    Feb 2005
    Location
    fremantle wa
    Age
    56
    Posts
    0
    Post Thanks / Like

    Default pool earth

    g'day dan
    sounds like you got a concrete pool.that earth wire sticking out of the ground will be bonded onto the reo mesh of the pool structure.
    by law it must be connected to the earth system of the premesis
    it should run back to your switchboard but have rarely seen this done it is usually just connected to the earth at your pool pump outlet
    having said all that best to get a sparky in

  4. #4
    Join Date
    Jul 2000
    Location
    Drop Bear Capital of Gippsland (Lang Lang) Vic Australia
    Age
    75
    Posts
    2,238
    Post Thanks / Like

    Default

    I thought pool lights were all low voltage and isolated from the main supply, we had a 12v system when we had a pool.
    Stupidity kills. Absolute stupidity kills absolutely.

  5. #5
    Join Date
    Oct 2006
    Location
    ACT
    Posts
    102
    Post Thanks / Like

    Default

    The lights are 12v as I have 2 transformers that I need to get installed.
    Im assuming the earth is to do with the lights

Similar Threads

  1. Pool Renovation Blog
    By spartan in forum LANDSCAPING, GARDENING, OUTDOORS
    Replies: 15
    Last Post: 1st October 2006, 06:01 PM
  2. Pool Decking
    By StuartN in forum DECKING
    Replies: 5
    Last Post: 1st September 2006, 12:08 PM
  3. pool deck stair ideas
    By lmcmali in forum POOLS, SPA & WATER FEATURES
    Replies: 0
    Last Post: 6th June 2006, 05:06 AM
  4. Planning a Pool Deck
    By Clive McF in forum DECKING
    Replies: 6
    Last Post: 14th May 2006, 12:35 AM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •