Electrical cable to the new shed. Sparkies?
I want to install a sub board in a shed 120m away from domestic premises in a rural residential area.
The cable run would be 120m from board to board.
The supply to the house is 2phase rural. (phases are 180° apart)
On the sub board I want to have one lighting circuit & 3 power circuits.
The maximum on the lighting circuit, including fans would not exceed 2400watts (10amps) with everything on at once.
The maximum on the power circuits would not exceed 6Hp in motors at once, allow 4800watts (20amps).
The cable will be in a conduit underground for 110m.
It would be best if we could run both phases to the shed & split/balance the load across them.
My question is ‘what cable do I order?’
I want to dig the trench & lay the cable & conduit & then have a registered sparky finish the job.
If I do the dirty work, I can afford to spend more money on the cable.
Any help would be appreciated.
PS. I don't need a lecture about the dangers of electricity.:rolleyes:
I've been working with it for 28 years. ;)
Is the Earth Wire Required?
Cliff,
Is the EARTH Wire required?
Can you get away without it,
and put down an EARTH Steak.....................OK!!!!! I know Stake:p :p
Something to chew over:confused: :o