Mate you have the same problem as before
https://www.woodworkforums.com.au/showthread.php?t=71539
Two things IMO it can be
!/WIreing
If you plug a another appliance into any Power point on the circuit that keeps tripping and the RCD don't trip Its not wiring its probably the Band saw.
Yes, it is the same problem as before but we thought it was the power wires and did not realise it only happened when the bandsaw was connected.
2/ The RCD is detecting a low resistance between the neutral and earth in the appliance
IE when you switch off the power point the switch is only in the active conductor so it still sees the fault between neutral and earth.
A sparkie has a measuring instrument Commonly called a MEGGA that measures Insulation resistance.
You problem would be found within a few minutes.
But as you said you are having trouble getting one My suggestion if possible is to take the band saw to them