Circuit breaker / Wire Size combo
Double checking on lecco's advice. I don't trust them. I have already had to throw out hundreds of dollars worth of parts on this job already.Two lecco's say 2 different things.
Heres the basic layout
3Phase to main board 80A I think
63A c/b in main board for workshop
25 sq mm 4C+E underground to workshop, run is 45mts.
Workshop has main distribution board with RCD and c/b to feed 3 sub boards + A/C unit
This is where i start getting different answers from lecco's
Length of run from distribution board to sub boards is
Sub Board 1 is 7mts
Sub board 2 is 1Mtr
Sub Board 3 is 12Mts
As it is steel framed building all cables are run in 25mm conduit
One lecco says 6 sq mm is sufficent between sub boards
Other says 10 sq mm between boards
:?
Each sub board will run 63A c/b
4 X 3ph 20A circuits
3 X 1Ph 15A circuits
2 X 1Ph 10A circuits
1 X 10A Light circuit
Both are saying I dont really need 63A c/b on subboards 40A will do the job. I think the reason they are saying 40A is because of the price difference with 63A being twice the price for c/b and 4 X the price for RCD. I dont think that they understand that this is 'MY SHED' and budget is not an issue ( well within reason). After doing the maths 40A would be cutting it a little fine for my likings on two of the sub boards. I do not want to go down the path of having to think about how much I am running all the time. Needless to say I am running some pretty serious machinery to want that much power.