Originally Posted by
Schtoo
Because the HV is 3 phase, pure and simple.
The LV (under 1,000V) is 3 phase and neutral. :D
The LV side of the transformer is connected in a 'star' configuration. Each wire comes in, goes through the load (say, your toaster) and connects to the other 2 active wires. The neutral is formed in the middle of the 3 pointed star.
If you have a 3 phase device, it's often connected in a 'delta' configuration, where each wire comes in, goes through the load (motor windings?) and connects to one other wire. The whole thing looks like a triangle, hence the delta name. There is no neutral formed in this type of connection, since 3 phase does not need a neutral.
In delta connections, the voltage is 415V between each wire. In star, the voltage is 240V between each wire and the other two wires/neutral point.
For a picture, draw a 3 lines meeting in the middle. Halfway along each line draw a squiggle. The squiggle are toasters, the meeting point the neutral. This is star.
Draw a triangle, and draw squiggles between each point. The squiggles are motor windings, and each point is each incoming wire of the 3 phases. This is delta.
Does that help, or do I need to draw you a schematic? ;)